All of a sudden.. 2 days ago, when I turn off my kitchen pendent they go to off then 1 second later they come back on again at extremely low output

c4 still thinks they are off and the puks report zero usage but they are still on albeit very very low

afaik nothing has changed in the system 

Share this post


Link to post
Share on other sites

If this is a newer generation dimmer. You can try pressing the  top button 9 times. Bottom 4 times then the 9 times.

 

If no change i will still try higher wattage led. 6watt vs 10 watt won't break the bill

Share this post


Link to post
Share on other sites

Did the light switch originally feed more that one light?

If you switch off all the lights in the room are they still dim?

Is there a neutral feed to the PUK?

Minimum load on the 240V PUK is 10W and LEDs are not recommended on non neutral connections.

 

Share this post


Link to post
Share on other sites

the puk has only ever fed these two pendent lights

they remain on (dimmed) when all other lights are off

not sure about the neutral, I will have to ask the spark

each LED is 6W and there are two (one in each pendent)

Share this post


Link to post
Share on other sites

So did you ever reset the dimmer?  I've had issues with screwed up maximums that a reset fixed.  I think the same could happen with minimums.  Not sure about pucks though

Share this post


Link to post
Share on other sites
On 02/01/2017 at 10:46 PM, Stuart England said:

the puk has only ever fed these two pendent lights

they remain on (dimmed) when all other lights are off

not sure about the neutral, I will have to ask the spark

each LED is 6W and there are two (one in each pendent)

Try changing one of the lamps (bulbs) to a non LED one and see if the LED one is still 'on' when the PUK is off.

Share this post


Link to post
Share on other sites

I've seen it happen a few times ... you think you got away with being close to minimum load and then a few days / weeks later the LEDs won't dim all the way down. The load the LEDs provide probably reduces when they have been 'run in'.

I would check with your electrician to see if there is a neutral connection to the PUK.

Share this post


Link to post
Share on other sites