Wiring directly into a smoke alarm is a bad idea.

 

They're a rated safety device, and by rewiring one, you're removing the rating, which in theory could have consequences.

 

Firex offers a relay designed specifically for what you're trying to do:

 

http://www.electricbargainstores.com/product-p/firex-501.htm

 

You wire it the same as any of the fire alarms, and it has outputs for an automation (or other) system.

 

RyanE

Link to comment
Share on other sites

First of all, since you're wiring it as a contact in on the Control4 system, you're not using the relay output to power a 120V device.

 

That means, don't wire the blue 'COM' wire to the black wire.  It should be +12V from the controller.

 

The NO (Orange) wire should be wired to a contact input ('SIG') on the Control4 system.  The NC (Yellow) wire should be not connected.

 

I think...

 

:)

 

RyanE

 

Edited to Add: No, they don't go to the NC / NO terminals on the Control4 system.  NC/NO/COM on the Control4 system are for a relay output.  You want to wire this to the contact *input* on the Control4 system.

Link to comment
Share on other sites

I believe it should go like this:

 

(relay module)  (Control4 Controller)

Blue (COM)   --> C4 +12V

Orange (NO)  --> C4 SIG input

Yellow (NC) --> Unused

Grey (+9V)  --> Unused

 

You use the Control4's own +12V to it's SIG input to indicate smoke.  No +12V, no smoke.

 

The reason you use Control4's +12V is that it's referenced to Control4's internal ground.  The +9V from the module is not referenced to Control4's ground, so won't likely work.

 

RyanE

Link to comment
Share on other sites

For the +9V to work, you'd have to also have a GND output from the module, which you would tie to Control4's GND contact.

 

As this is a 'dry relay' output, you supply the +12V from Control4, it goes back into the SIG, that's your circuit.

 

RyanE

Link to comment
Share on other sites

Yes, you *could* use the yellow wire to indicate that it's not in alarm, but what's the point?  It's a non-latching relay.

 

If the NO pair is not closed, the NC pair is.

 

And if you're wiring it up for 'confirmation' as proposed, the yellow wire does not *go* to NC, it *is* NC.  It would have to be wired to a different 'SIG' input.

 

RyanE