Integrate with BACNET Server


coreautomation

Recommended Posts

Hello to all of you out there!

This is the first time i post in c4forums so hope to have a good start!

We have been asked by a client to integrate there HVAC installation with Control4. The HVAC systems is controlled by a Tridium Niagara4 appliance called JACE. (https://www.tridium.com/en/products-services/niagara4#JACE8000). This product, apart from controlling your HVAC systems can also interface with other systems via BACNET, MODBUS, LON (server and client) and KNX (client only) protocols via RS485 and IP interfaces. We are thinking of setting up JACE as a BACNET server via IP in order for other devices, such as C4 controller to interface with it as BACNET clients, in order to read and write the published datapoints in Bacnet (similarly like control4 would interface with a KNX subsystem). 

We would like to know if there is any way to install a bacnet client (over IP) to a C4 controller? If not how would you interface an HVAC system that can communicate via the above described protocols and methods?

Many thanks in advance to all!

Regards

Kostas

www.core-automation.gr

Link to comment
Share on other sites

  • 3 weeks later...

On 3/8/2020 at 11:41 PM, coreautomation said:

Hello to all of you out there!

This is the first time i post in c4forums so hope to have a good start!

We have been asked by a client to integrate there HVAC installation with Control4. The HVAC systems is controlled by a Tridium Niagara4 appliance called JACE. (https://www.tridium.com/en/products-services/niagara4#JACE8000). This product, apart from controlling your HVAC systems can also interface with other systems via BACNET, MODBUS, LON (server and client) and KNX (client only) protocols via RS485 and IP interfaces. We are thinking of setting up JACE as a BACNET server via IP in order for other devices, such as C4 controller to interface with it as BACNET clients, in order to read and write the published datapoints in Bacnet (similarly like control4 would interface with a KNX subsystem). 

We would like to know if there is any way to install a bacnet client (over IP) to a C4 controller? If not how would you interface an HVAC system that can communicate via the above described protocols and methods?

Many thanks in advance to all!

Regards

Kostas

www.core-automation.gr

Control4 have a driver for fieldserver which is a BACnet over IP gateway.  Note that you will need to program the BMS system to be suitable for the driver's requirements.  Search the Control4 knowledgebase for fieldserver and you'll find the driver and installation guide.

Link to comment
Share on other sites

16 minutes ago, alanchow said:

Control4 have a driver for fieldserver which is a BACnet over IP gateway.  Note that you will need to program the BMS system to be suitable for the driver's requirements.  Search the Control4 knowledgebase for fieldserver and you'll find the driver and installation guide.

Dear alanchow

many thanks for your help above!

We are aware about quickserver gateway and we will consider installing this if no other options are available. 

But we are mostly looking for a bacnet driver for C4 in a way that C4 will act as a bacnet client to a bacnet network over IP. In that way a C4 controller would communicate directly with the bacnet network so there would be no need for an intermediate gateway such as the fieldserver...

Any ideas if there is such a driver out there?

Many thanks once again!

Link to comment
Share on other sites

29 minutes ago, coreautomation said:

Dear alanchow

many thanks for your help above!

We are aware about quickserver gateway and we will consider installing this if no other options are available. 

But we are mostly looking for a bacnet driver for C4 in a way that C4 will act as a bacnet client to a bacnet network over IP. In that way a C4 controller would communicate directly with the bacnet network so there would be no need for an intermediate gateway such as the fieldserver...

Any ideas if there is such a driver out there?

Many thanks once again!

doesn't exist sorry.

Link to comment
Share on other sites

  • 4 months later...
On 3/29/2020 at 2:23 PM, alanchow said:

Control4 have a driver for fieldserver which is a BACnet over IP gateway.  Note that you will need to program the BMS system to be suitable for the driver's requirements.  Search the Control4 knowledgebase for fieldserver and you'll find the driver and installation guide.

Hi Dears

By this way can i control Control4 actuators by BMS system ? 

I mean is it two way integration ??

 

 

Thanks

 

Link to comment
Share on other sites

This thread is quite old. Please consider starting a new thread rather than reviving this one.

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use.