Tim Posted October 30, 2008 Share Posted October 30, 2008 I have seen many discussions on fireplace connects on the forum, but I'm not seeing how to fix my issue- or, I'm missing something.I have two fireplaces. Both are setup with a low-voltage wire running from the fireplace to a standard house switch to control turning the unit on and off manually. Behide the house switch I also have a cat5 line running from the wall location to a HC. I would like to replace the house switch with a 2-button to a) control the fireplace through automation and have the ability to still turn the unit on and off manually. On a third fireplace, I had the luxury of having 110V connection. I wired the 2-button normally and connected the fireplace low-voltage to the cat5 and it works really well.Unfortunately for the two fireplaces mentioned above, I don’t have the ability to get to a 110v power connection.Any suggestion?Tim Link to comment Share on other sites More sharing options...
henniae Posted October 30, 2008 Share Posted October 30, 2008 The 2 button will run of of low voltage (36 volts to be exact). C4 sells a low voltage transformer part number C4-KPS36-M-B. You could use a few of the conductors of the Cat-5 to run power to the 2 button from the transformer and a few other conductors to run the fireplace control down to your controller. Program the 2 button to control the relay on your controller. Link to comment Share on other sites More sharing options...
Tim Posted October 31, 2008 Author Share Posted October 31, 2008 Thanks Alan... I will look into the C4-KPS36-M-B.Tim Link to comment Share on other sites More sharing options...