    ezadok reacted to C4 User in DSC NEO Integration   
    I just spoke to DSC Connect24 support regarding integrating my DSC Neo into both Control4 and Connect24. Note the I have the TL280LE Communicator. When your central monitoring station is programming your communicator using Connect24, under the INTERACTIVE tab, they need to:
    - set Integration over Ethernet
    - Enter the C4 controller IP address
    - set Notification port to 3072
    - set Polling port to 3073
    - set Real Time Notifications to ON
    The above settings must be set by your Central Monitoring Station using Connect24. All the other parameters and keys necessary to complete the integration can be read at the keypad for integrating your C4 system into your DSC Neo panel.
  2. Like
    ezadok reacted to jamesc4 in DSC NEO Integration   
    Central station has an account with Connect24 
    tell them they have to go to the interactive tab
    see the specs
    Remote activating and programming through C24 Communications
×
×