sofakng Posted February 13, 2019 Share Posted February 13, 2019 Does anybody know the voltage of the EA3 and I/O extender relays? I believe they are both 24v but I’m not 100% sure. The manually specifies that as the “max” voltage. For example, if a Control4 driver turns the relay on, does than mean that 24v will be sent across COM and NO (normally open)? (and likewise, 0v will be sent when the relay is off) Link to comment Share on other sites More sharing options...
twmoonly Posted February 13, 2019 Share Posted February 13, 2019 those relays don't output voltage. 24v max is the maximum the relay will handle if you send voltage in it. What are you trying to do? Link to comment Share on other sites More sharing options...
sofakng Posted February 13, 2019 Author Share Posted February 13, 2019 Hmmm, maybe I’m confusing the contact sensor ports and the relays? I’m trying to connect a Control4 controller (EA3/IO extender) to another relay and be able to turn it on and off. For example, I thought that the C4 relay would send 24v when “on” and 0v when “off”. The goal is to control a 120v device (on/off) using Control4 and wires. I know there are several wireless outlet relays (WeMo, etc) but I’m trying to find/build something hardwired. Does that make sense? Link to comment Share on other sites More sharing options...
twmoonly Posted February 13, 2019 Share Posted February 13, 2019 You can do that, get a power supply, pass the negative through the relay on control4 then to device. send the positive directly to device this way you are not limited on the ca[pacity of the control4 relays. You cant pass 120v through the control4 relays. You could uses something like this https://www.amazon.com/Enclosed-Relay-Class-Dry-Contact/dp/B00788AN4K Link to comment Share on other sites More sharing options...
twmoonly Posted February 13, 2019 Share Posted February 13, 2019 or this https://www.amazon.com/Functional-Devices-RIBU1C-Enclosed-Pilot/dp/B000LESCI2/ref=pd_lpo_vtph_328_bs_lp_t_1?_encoding=UTF8&psc=1&refRID=3Z652ZJ5003F0DS6M7M6 Link to comment Share on other sites More sharing options...
sofakng Posted February 14, 2019 Author Share Posted February 14, 2019 Thank you so much for the information. Is the relay basically an electronic switch? For example, you can connect up to 24v into the COM terminal and then it will go out the NO/NC terminals depending if the controller has it on or off? I'm thinking of relays that are used for a low voltage (i.e. 24v) to control a high voltage (120v) device? Can you explain how it works better? Link to comment Share on other sites More sharing options...
twmoonly Posted February 14, 2019 Share Posted February 14, 2019 Thank you so much for the information. Is the relay basically an electronic switch? For example, you can connect up to 24v into the COM terminal and then it will go out the NO/NC terminals depending if the controller has it on or off? I'm thinking of relays that are used for a low voltage (i.e. 24v) to control a high voltage (120v) device? Can you explain how it works better? Yes the relay is just a switch. If you want low voltage relay to control 120v you would need that second item I posted. Low voltage wires to Control4 and 120v wires to device. What is the application?Sent from my iPhone using Tapatalk Link to comment Share on other sites More sharing options...
sofakng Posted February 14, 2019 Author Share Posted February 14, 2019 The application is that I’m trying to control power to a PC. (there are other ways of controlling a PC, but I’m interested in completely removing power, etc) Would something like this work? http://www.powerswitchtail.com/new-powerswitch-tail-3 It’s described as a DC-actuated power cord with built-in 5vdc power supply. I’m wondering if I can connect the +5v from the power cord to the Control4 relay, and then back into the power cord control signal. When Control4 activates the relay, the +5v will turn on the power cord. Does that make sense? Thanks again for all of your help! Link to comment Share on other sites More sharing options...
Unsocialtoaster Posted February 15, 2019 Share Posted February 15, 2019 Contact Maximum Current Draw EA-3 / EA-5 30VDC, 1.25A maximum HC-800 12VDC 1.25A / Shared across all outputs HC-250 12VDC 1.25A HC-500 12VDC Max 250ma / Shared across all outputs HC-300 12VDC Max 250ma Home Theater Controller 12VDC 750ma Media Controller 12VDC 1.25A / Shared across all outputs IO Extender 12VDC 1.25A / Shared across all outputs Contact/Relay Extender 500ma / Shared across all contacts Relay Max Voltage Throughput EA-3 / EA-5 AC: 36V, 2A max / DC: 24V, 2A max HC-800 AC - 36V, 2A / DC - 24V HC-250 AC - 36V, 2A / DC - 24V HC-500 AC - 36V, 2A / DC - 24V HC-300 AC - 36V, 2A / DC - 24V Home Theater Controller AC - 36V, 2A / DC - 24V Media Controller AC - 36V, 2A / DC - 24V IO Extender AC - 36V, 2A / DC - 24V Contact/Relay Extender AC - 36V, 2A / DC - 24V Link to comment Share on other sites More sharing options...
Unsocialtoaster Posted February 15, 2019 Share Posted February 15, 2019 20 hours ago, sofakng said: I’m wondering if I can connect the +5v from the power cord to the Control4 relay, and then back into the power cord control signal. When Control4 activates the relay, the +5v will turn on the power cord. Does that make sense? I'm 99% sure that will work! Link to comment Share on other sites More sharing options...
twmoonly Posted February 15, 2019 Share Posted February 15, 2019 Yes that will work Link to comment Share on other sites More sharing options...
sofakng Posted February 16, 2019 Author Share Posted February 16, 2019 Thank you so much for the help everybody. I really learned a lot. Link to comment Share on other sites More sharing options...
Pounce Posted February 16, 2019 Share Posted February 16, 2019 On 2/14/2019 at 10:43 AM, sofakng said: The application is that I’m trying to control power to a PC https://www.digital-loggers.com/pro.html Link to comment Share on other sites More sharing options...
mallom Posted February 16, 2019 Share Posted February 16, 2019 https://www.digital-loggers.com/pro.html +1And free C4 drivers Link to comment Share on other sites More sharing options...