2 hours ago, RAV said:

Can anybody explain why the ideal goal isn't 60.0Hz, or 50.0Hz ?

Forced 1% slowdown. There's several explanations/myths around the ORIGIN of it (most commonly the move from black and white to colour TV) as well as what it actually influences (some pretty funny ones out there).

The simple version of the reason is that at a 1/10th percent slowdown you prevent resonating/interfering frequencies.

Link to comment
Share on other sites

18 hours ago, Cyknight said:

This comes up time and time again. Your generator needs to be tuned to the right frequency.

If you electrician/installer states it is; he's wrong.

Generator at a proper frequency of 59.94 means no issues with the lights.

my electrician said it hovers between 59.7-60.02hz and would look to see if there is a parameter to make it fixed.  he said the frequency naturally dips as it becomes loaded to varying degrees of demand and its always trying to maintain 60hz.  He said if it goes too far under or over it will shut down to prevent damage.

Do you have documentation on how to set a Generac to 59.94?  He is going to ask around but this is the first he is hearing about it...

Link to comment
Share on other sites

This thread is quite old. Please consider starting a new thread rather than reviving this one.

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...

Important Information

By using this site, you agree to our Terms of Use.